Good evening guys!How can i calculate the expansion vessel in a water circuit?No drawings available.

NoNickName
27-09-2010, 07:04 PM
Warm water heating?

HARRY 7
27-09-2010, 07:14 PM
Hi NoNickname! heat pump water chiller.

NoNickName
27-09-2010, 07:28 PM
open vase or closed vase?

HARRY 7
27-09-2010, 07:33 PM
closed vessel.

NoNickName
27-09-2010, 07:35 PM
open vessel

http://www.tempcoblog.it/wp-content/uploads/2009/09/vaso-aperto1-300x34.jpg

closed vessel with no diaphragm

http://www.tempcoblog.it/wp-content/uploads/2009/09/vaso-chiuso-s-diafr1-300x66.jpg

closed vessel with diaphragm:

http://www.tempcoblog.it/wp-content/uploads/2009/09/vaso-chiuso-c-diafr-300x66.jpg

Vv = expansion vessel volume (L)
Vw = volume of water in the plant (L)
v1 = specific volume of water at the lowest temperature t1 (m3 / kg)
v2 = specific volume of water at the highest temperature t2 (m3 / kg)
α = expansion coefficient of metals
- for steel α = 1,2 . 10-5 (1/K)
- for copper α = 1,65 10-5 (1/K)


http://www.tempcoblog.it/1596/il-vaso-di-espansione/

t1 is generally the temperature to which the system is charged (10-15°C)

HARRY 7
27-09-2010, 07:37 PM
How can i find the volume of water in the plant?

NoNickName
27-09-2010, 07:43 PM
How can i find the volume of water in the plant?

Charge it and measure the amount of water that goes into it. Or if already filled, empty the plant and measure the volume of water removed, by pouring it into a known volume.
I suppose you know how to calculate the volume of a solid.

HARRY 7
27-09-2010, 07:45 PM
It is a big plant nonickname.Any other way??

NoNickName
27-09-2010, 07:49 PM
You could inject a small amount of a tracing radioisotope into the main loop, and install an ultrasonic flowmeter on the main header. By measuring the time the radioisotope crosses the geiger sensor, multiplying by the average water flow measured by the flowmeter, you would be able to find the volume with reasonable accuracy.

HARRY 7
27-09-2010, 07:53 PM
A little difficult to do this.Is there any way to find it from the water pump?

NoNickName
27-09-2010, 07:57 PM
not that I know.

HARRY 7
27-09-2010, 08:23 PM
thanks for the replies nonickname:).
if anybody else can help?

Brian_UK
27-09-2010, 11:32 PM
Rough calculation of water quantity is normally by relating it to the system duty.

Have a look here, data mostly refers to heating but by using 30°C as maximum system temperature you can ache8ive an answer.

www.mikrofill.com/images/PDF/n-and-de-range.pdf

nike123
28-09-2010, 07:35 AM
thanks for the replies nonickname:).
if anybody else can help?
Measure pipe lengths and diameters. Collect volume data of equipment (chiller, fan-coils, puffer, etc). Calculate volume in each element and sum it. That is your volume for calculation of vessel.
This is good site for calculation of vessels:
http://87.128.225.163/index.php

Software:
http://www.reflex.de/fileadmin/user_upload/exe/reflex4_de.exe

NoNickName
28-09-2010, 07:36 AM
Brian, his system is existing already, and is a warm water plant.

HARRY 7
28-09-2010, 04:16 PM
Thanks all of you for replys guys.Brian i used 40C.It is a heat pump.