View Full Version : code 46



avtrans
21-09-2010, 06:04 AM
i need help whit alarm code 46 cant you explain ?

avtrans
21-09-2010, 06:06 AM
cant you explain alarm code 46

abbsnowman
21-09-2010, 06:27 AM
If this temperature differential exceeds a user
defined number of degrees for a user defined period
of time, Alarm Code 46 CHECK AIR FLOW is
generated as a check alarm. If the trailer is
equipped with a door switch and the feature is
enabled, monitoring ceases when the door is
opened and is resumed 45 minutes after the door is
closed. When the unit enters a defrost cycle,
monitoring ceases and is resumed 45 minutes after
the defrost cycle terminates. Should the control
discharge temperature sensor or Spare sensor 1 fail
the Air Chute Detect feature is disabled.

Temperature Differential
Micro Rev All

HMI Rev All

Choices 1°F to 20°F in 0.1°F increments
1°C

Peter_1
22-09-2010, 08:06 PM
cant you explain alarm code 46

You expect an answer within 2 minutes, alarm code for what..?
I think this code says : hold one till someone has time to answer your question, this is not a chat room.