View Full Version : Heat pumps and Thermal expansion valves question



ctscasemod
13-09-2010, 01:12 AM
I was wondering...
I use Danfoss TE2 and TEX2 Expansion valves, witch are used for a wide range of applications from 0.14 to 5ton air conditioner by some interchangeable orifices for the needed capacity (1ton/2ton...).

Question:
In a heat pump we use two of these valves, so do we need both valves having a orifice or is only one needed!?


Thanks

mikeref
13-09-2010, 06:11 AM
Ctscasemod, if two valves are used then two orifices must also be used. Besides, the orifice strainer is the seat for the copper flare to seal against.

ctscasemod
13-09-2010, 10:52 AM
Ctscasemod, if two valves are used then two orifices must also be used. Besides, the orifice strainer is the seat for the copper flare to seal against.

Yes, otherwise the valve would have to be soldered, but are the two orifices the same size? Since I'm using TEX with internal reverse valve there are two orifices in series, so, wouldn't the output be reduced by them?

Thanks

nike123
13-09-2010, 11:04 AM
Yes, otherwise the valve would have to be soldered, but are the two orifices the same size? Since I'm using TEX with internal reverse valve there are two orifices in series, so, wouldn't the output be reduced by them?

Thanks

Danfoss TEX2 with internal reverse valve does not exist.

ctscasemod
13-09-2010, 11:16 AM
Danfoss TEX2 with internal reverse valve does not exist.

You're right, I've meant TE2
Thanks

nike123
13-09-2010, 11:19 AM
You're right, I've meant TE2
Thanks
Same thing!

ctscasemod
13-09-2010, 05:50 PM
Same thing!

Must have, I have a system runing one right now!

nike123
13-09-2010, 09:01 PM
http://www.ra.danfoss.com/TechnicalInfo/Literature/Manuals/01/DKRCCPDAA0A402.pdf

mikeref
14-09-2010, 05:28 AM
Must have, I have a system runing one right now!
Ah, hasn't been invented yet. Don't you mean external equalisation line?:confused: