hey guys im on site engineer at a call centre no air con tools on site with me,iv got u4 fault on 3 systems the temp dropped from 21 cooling to 16 i no what the fault is but what i dnt no is how to fix it any advice ?

andyc425
07-09-2010, 10:37 AM
iys daikin by the way and they were set on 21 cooling 22 heating

NoNickName
07-09-2010, 11:13 AM
Communication fault between indoor and outdoor

andyc425
07-09-2010, 11:14 AM
yeh i no the fault how do i fix it?

NoNickName
07-09-2010, 11:30 AM
Check communication between indoor and outdoor. Check wiring does not go along together with power cables. Switch off and on to try resetting communication.
If everything else fails, it may be the PCBs have suffered a power surge and the three need to be replaced.

andyc425
07-09-2010, 12:44 PM
nice one fella job done