Is oil trap really necessary?:D
http://www.fanzo.org/forum/download/file.php?id=29262&mode=view

coolhibby1875
03-09-2010, 07:47 PM
not really, i prefer a double riser!

Eeram
05-09-2010, 05:25 PM
Oil trap or double riser.

Depends on the system. I had systems where the liquid is so "dry", we need to inject oil in the liquid line to let solenoids and electronic expansion valves operating freely. On screw systems

3/8" oil line on solenoid valve, 3 seconds on, 20 minutes off.

nike123
05-09-2010, 06:13 PM
Common guys! Chill out.:eek:

No sense for humor, or simple nerds?

monkey spanners
05-09-2010, 06:59 PM
Not if you drain all the oil out first.