Following are the observation for my R-134a system two samples (say Sample A Vs Sample B)
(Sample A is OK sample with desired Cooling )
1. Sample B is having less cooling problem
2. Sample B discharge, drier, suction, Compresor temperatures are higher than that of Sample A.
Subcooling of sample B is lesser than that of Sample A.
The Pressures are not measured as both the samples are at differnt locations.
Both the samples are of same specifications
Evaporator, condenser, capillary and compressor are same in both the samples.
What i am suspecting is less refrigerant qty leading towards less cooling in Sample B.
Thanks
Amit Saxena