View Full Version : Daikin Urura srara & U0



TeMpL
24-08-2010, 04:27 PM
Please help. Is this normal? :confused:
got U0 error aFter 2 jears (no more than 1000-1500 hours of operation)

Leak in the system? Or is this normal?
Or possible EVV Failure?

Unit is not heating/nor colling just blowing air... compresor starts both blowers too. (on inner and outer unit). :confused:

thanks for info!!!

Brian_UK
24-08-2010, 11:32 PM
Could be either, faults may not be normal but can happen.

You need an AC technician to check the unit.

TeMpL
25-08-2010, 06:58 AM
Shuld leak be vissible (oil stain) or not?

TeMpL
25-08-2010, 07:39 AM
Shuld leak be vissible (oil stain) or not?

ok i found oil/leak on "big" pipe outer on compressor.
:(

ktm
25-08-2010, 01:36 PM
U mean the suction? Is it on a fitting or a crack on a pipe? What the operating pressures like?

Brian_UK
25-08-2010, 06:46 PM
U mean the suction? Is it on a fitting or a crack on a pipe? What the operating pressures like?
TeMpL is not a refrigeration man but an end user I believe.

ktm
25-08-2010, 07:36 PM
Ah rite sorry brian. Well then get someone to look at it who knows what they are looking at so. I don't think I'm a doctor so I go to one when I'm sick!!!

brunstar
25-08-2010, 11:06 PM
yeah well if it is on the suction line outside the unit then you should get your installer back as it looks like he should have pressure tested his installation.