JIMMY SMITH
24-08-2010, 05:35 AM
what is the full load amperage of a copeland compressor model CRN5 0500 TF5 270
nike123
24-08-2010, 09:52 AM
what is the full load amperage of a copeland compressor model CRN5 0500 TF5 270
LRA= 130A
MCC= 30A
RLA (Contactor sizing)= 21.4A
RLA (Wire and breaker sizing)= 19,2A
At 7,2°C/54,4°C 10K superheat = 17,7A
At -6,7°C/48,9°C 20K superheat = 14,4A