View Full Version : DWM DKSLA R/12 Copeland
krnjad
23-08-2010, 09:35 AM
Hello everyone. We need the data on this compressor precisely its strength to 0, -5, -10, -15, -20.
nike123
23-08-2010, 04:27 PM
Nema tog modela. Provjeri oznaku.
There is no such model # in Copeland data base. Find correct model #.
Correction, it is such model number but without "R/12" part!
krnjad
24-08-2010, 03:48 PM
Thanks team Copeland replacement for him is 15x R 134
nike123
24-08-2010, 04:58 PM
D= DWM Copeland
K= 2 cylinder
S= long stroke
L= 9,1 m3/ displacemant at 1450 o/min (50hz)
A= model variation (A-P)
-= separator
15= motor size (15 or 20 )
X= POE oil
http://i37.tinypic.com/34nfsio.jpg
What is use of your compressor? By asked conditions i suppose MT (medium temperature) refrigeration.
http://i37.tinypic.com/3026hox.jpg
krnjad
24-08-2010, 07:50 PM
Milk cooling tank was used to 1200l.
Can you replace it DANFOSS-Maneurop MT 28?
nike123
24-08-2010, 08:26 PM
Milk cooling tank was used to 1200l.
Can you replace it DANFOSS-Maneurop MT 28?
If you wish to replace it and still use R12 with him than you need MT 36 because it has simmilar displacement (10,6 m^3/h)
What is cooling capacity of evaporator?
krnjad
24-08-2010, 08:36 PM
Milk cooling tank was used to 1200l,but the day bringing 500l of milk.
krnjad
24-08-2010, 09:18 PM
I want to replace 150 R/12 DKSLA DWM Copeland is defective for the new DANFOSS Maneurop MT-28 to R22.
krnjad
24-08-2010, 09:39 PM
:rolleyes:
krnjad
24-08-2010, 09:49 PM
I want to change the DWM DKSL 150 R 12 for the new Danfoss Maneurop MT 28 R 22
nike123
24-08-2010, 09:50 PM
Koji češ plin koristit?
It is not clear what refrigerant you plan to use.
If you are going to use R22 instead of R134 or R12 than for same capacity as original compressor (if that is original one) you need MT22 compressor and new TXV like TEX2 with 02 orifice.
Mislim da si takav odgovor već dobio na Fanzi.
krnjad
25-08-2010, 09:07 AM
I'll take the R22, which goes with the MT 28 course that will change the valve, filter and nozzle
Excuse the spelling, I write it using Google Translate
krnjad
25-08-2010, 03:08 PM
Hello everyone. We need the data on this compressor DWM DKSLA 150 R/12 Copeland precisely its strength to 0, -5, -10, -15, -20.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.