View Full Version : Copper pipe for Mitsubishi R410a Models



Chris2005
11-06-2005, 08:44 PM
Hi all.

What grade of copper is needed for mitsubishi R410a models we have 4 MSH-GA60VB wall mounted units to fit on monday morning ..
We have not used these units before with r410a refrigerant but after reading afew articles on the net i am a bit concerned that we have been supplied with soft copper 21swg by our supplier for the job.

Will this stand the pressure ..

Thanks chris.. :confused:

rbartlett
11-06-2005, 09:05 PM
just use normal fridge copper but use the concentric flare'er

cheers

richard

tdmartin7
26-03-2007, 07:50 PM
What is a CONCENTRIC flare tool? I called our local RSD and they are not sure, does it make a double wall?

Electrocoolman
27-03-2007, 11:59 AM
What is a CONCENTRIC flare tool? I called our local RSD and they are not sure, does it make a double wall?

I think ECCENTRIC flaring tool is the correct name.
It is not an equal cone, but is offset.
The cone sweeps around as it flares and you end up with a very polished surface on the flare, and produces a much stronger flare.

michael7
28-03-2007, 05:11 PM
Normal fridge pipe is OK upto 3/4" however, check the charts in the HRP book to make sure the wall thickness is OK as you go up in size. I am using 16g on any thing over 3/4" if it's available.

nikos topts
26-01-2008, 01:30 AM
hi chris i ve just entered re. i ve installated some of these{msz 60gb va} for example. your copper pipe is 5/8 and 1/4 .the thickness of your pipes must be 1.0mm for 5/8 and 0.8mm for 1/4. use a good eccentric flaring tool for not having leaks. {read carefully the installation manual and you wont have any problems!!!!