as above, fridge is set for plus two,
terminates at minus two,
fridge is eurofrigo c2500 xts
any ideas?

frank
17-08-2010, 12:15 PM
Is this a fridge on a lorry?

aircon50
17-08-2010, 01:47 PM
Hi Steve
From memory all the Eurofrigo units that used to work on overshot the set point. The important bit, for me, was that they cut out. I compensated by adjusting the set point accordingly.
I used to have wiring diags, etc, but left them behind when I left UK.
Out of interest, I guess from your user name, you are with a Carrier dealer.
If you are Steve A...... please PM me! Got some catching up to do!
Regards. Graham

Electrocoolman
17-08-2010, 02:23 PM
Is it controlled by an electronic controller?
Does it cut out at SP (-) Hysteresis

If so the controller is possibly set up for heating and the relay contacts (Change over) are reverse wired.

A normal refrigeration control cuts out at SP and cuts in at SP (+) Hyst.