14-08-2010, 06:37 AM
A 4.H.P. Belcor split-system had the evaporator changed to Electra some time ago.The capillary (correctly sized) is on the condensing unit.The temperature of the returning liquid on a 20 foot run in 3/8" tube is neither hot nor cold, but the returning suction is "sweating" and at 78PSI with a head pressure of 300PSI at 45 Degrees C ambient. Normally you get a good "feel" for how a system is performing by the temperature of the suction and liquid lines.I have seen this a couple of times in the past but don't understand what causes it.There is no capillary tube in the evaporator.
After changing the compressor and capillary the operating pressures are the same as is the temperature but the compressor does not cut out on klixon intermittently now even in the afternoon when ambient temperature peaks.
After changing the compressor and capillary the operating pressures are the same as is the temperature but the compressor does not cut out on klixon intermittently now even in the afternoon when ambient temperature peaks.