lynark
09-08-2010, 09:24 PM
hi guys,

i have a vilter compressor running on R22 for ice builder with 4 F suction temp and 112 F condensing temp. now the problem is worn out on the outer seat of the discharge valve. What do you think made this? any one can help?

thank you

RANGER1
09-08-2010, 09:28 PM
Is it a new system with a lot of steel pipe ?
What model of Vilter & type of discharge valve ie ring type valve plate ?

lynark
09-08-2010, 10:02 PM
vilter 450. the high suction safety head was already replace for R22 application. but still there's a problem on the worn out discharge valve

lynark
09-08-2010, 10:04 PM
Is it a new system with a lot of steel pipe ?
What model of Vilter & type of discharge valve ie ring type valve plate ?


no. its been running for 3 yrs. but they haven't solve the worn out problem.

Waynexb
15-08-2010, 06:41 AM
we have had it where the discharge saftey spring had lost their tension alowing the discharge plate to bounce.is it an old machine

RANGER1
15-08-2010, 10:09 AM
I have seen a case of the discharge valve rings actually wearing right through the valve plates .
This was a R22 plant with Sabroe compressors .
The plant was new & put it down to steel pipe dust,scale etc .
Replaced once & all OK .
Didn't seem to wear anything else but discharge valves .
Maybe this happened to you .

lynark
15-08-2010, 04:33 PM
hi ranger1,

the worn out safety was already replace we are monitoring now the operating temperature/pressure hopefully we can find the root cause of the problem. because there are two ice builder. the ice builder 1 is running without problem for so many years on the ice builder 2 ( new one but total replica of the ice builder 1 ). that is why can't seem to understand what went wrong


thank you

lynark

lynark
20-08-2010, 02:05 PM
hi ranger1,

the worn out safety was already replace we are monitoring now the operating temperature/pressure hopefully we can find the root cause of the problem. because there are two ice builder. the ice builder 1 is running without problem for so many years on the ice builder 2 ( new one but total replica of the ice builder 1 ). that is why can't seem to understand what went wrong


thank you

lynark


hi Ranger1,

forgot to mention there are 3 compressor with 1 common suction header and liquid header.
also got the running details.

suction pressure: 21 psi
discharge pressure: 255 psi
ampere: 101

suction pressure: 19 psi
discharge pressure: 215 psi
ampere: 96

the design specs of ice builder are 4 F (27 psi ) suction and 112 F condensing temp.


thank you

lynark

RANGER1
20-08-2010, 10:08 PM
Can you post picture of worn out discharge valve and/or a vilter part number .
You also have 255 psi discharge on one compressor , is the an error .

lynark
22-08-2010, 02:11 AM
Can you post picture of worn out discharge valve and/or a vilter part number .
You also have 255 psi discharge on one compressor , is the an error .


hi ranger1,

ok i'll try to pose some pictures. The outer ring of the safety head is the one being worn out. part number 517 of vilter parts

But now the problem is got broken piston with lots of metal debris just open up the compressor yesterday to check the odd sounds its making. oil filter are full of black sludge so maybe the broken piston is due to lubrication failure but still checking the system.

about the discharge pressure, 255 psi is correct that the highest recorded pressure the lowest is 215 psi they give me.


thanks for the help


lynark