08-08-2010, 01:00 AM
Hello, Suhail here. We have an absorption chiller of 166 USRT on our site. We are facing problems in it. Two weeks before chiller got leakage in one of evaporator's tube. We contacted the vendor. Representative came to site, leakage rectified. After this maintenance work, we are facing the problem.The problem is that, Chiller starts normally. Steam increase accordingly. When temperature of the generator reaches to 150 degree c, steam flow becomes Zero while steam control valve remains open.

Please help me in this

suhail

rtamayo
08-08-2010, 05:07 AM
If I understand you have troubles with the steam line; you should check the steam trap.

eng_roshdy24
30-09-2010, 07:20 AM
would you please help me to find the Performance curve of your absorption chiller.
I mean the curve which is showing the relation between chilled water, cooling water temprature and cooling capacity.