I have a scroll compressor on a space pack that's alarming out (danfoss A24 fault), when I pull off the solenoid that's attached to the Emerson oil pot the alarm goes off but then comes back? Any idea's why this alarm is happening plz?
fowlie
04-08-2010, 07:30 PM
is it a low oil alarm for that compressor,is the oil level low with foaming in it,plus is it an low temp pack
improver No1
04-08-2010, 07:40 PM
the oil level is half way across the sight glass, and yes its a low temp pack.
thanks for ur reply
fowlie
04-08-2010, 07:51 PM
is the oil solenoid live and calling for oil as sometimes the liquid injection can open up to much and put liquid into the oil sep then the oil float,is it a traxoil float and if so what are the indicator lights showing
improver No1
04-08-2010, 08:01 PM
the oil solenoid is live because i can feel the magnetic pull on it when i pull it off, yeh its a traxoil float the light is green indicating ok.
fowlie
04-08-2010, 08:06 PM
if its live then theres a light to indicate that its calling for oil,it has a oil can symbol on it.is the alarm a24 for that comp or for something else as the oil float will show an alarm if its got a fault
improver No1
04-08-2010, 08:12 PM
yeh the a24 alarm code is for comp3 which is that comp
fowlie
04-08-2010, 08:14 PM
is the compressor running or just showing an alarm is it one of those large scrolls or just a small one
improver No1
04-08-2010, 08:35 PM
Its a small one the comp is not running
fowlie
04-08-2010, 08:40 PM
i take it the control circuit is okay through the hp/lp switches,if so i would say your oil float reg is fecked
improver No1
04-08-2010, 09:18 PM
Yeh there is only one hp/lp switch on the pack not individual comps, sound then pal I will get it changed
improver No1
04-08-2010, 09:18 PM
I will test the control circuit tomorrow
fowlie
04-08-2010, 09:27 PM
if its a new pack i would check the wiring as it wouldnt supprise me if it was wired up wrong although space packs are ushally well done
improver No1
05-08-2010, 12:08 PM
I got to site and the comp was alarming out Emerson oil pot was on amber again so I did the same took the solenoid off and reset it which made the comp run for about two hrs and then it tripped out the compressor again? So I think it's the Emerson oil pot?
tony--1
05-08-2010, 10:36 PM
is the comp full ov oil when it trips off ?
improver No1
06-08-2010, 06:28 AM
Yeh it is?
Animal
10-08-2010, 01:17 PM
Hi Guys, there was a problem with the Moulded Plugs that are used on the Traxoils, the connections were breaking internally, a updated loom was supplied that had soldered terminals instead of crimped ones, this sometimes caused Alarms even though the Oil levels were ok, if the pack is a couple of years old, this could be the problem, i think they were upgraded the middle of last year,