I'm working on a linde pack with a compressor that's been alarming out for 59weeks! I just can't clear the alarm, I push the contactor in and everything works and the crankcase heater cuts out which leads me to believe it's a control fault? Iv changed the klixon but still alarming iv tried following the wires but with no diagram this is difficult, can anyone help?

coolhibby1875
24-07-2010, 01:43 PM
the wiring on these packs are a nightmare, if its the type with switches on the panel door that turn compressors between off/on and auto, try there the switches alaways burn out, also common fault is bad neutrals, good luck!

graydog
26-07-2010, 09:50 AM
The PCB relay had blown!! oh well at least iv learnt something

monkey spanners
26-07-2010, 04:11 PM
Pleased you found the problem!

Jon