Hi guys

Can anyone tell me if you need to address the new Daikin VRV3 units on commissioning or do they set them selves up. As we have a unit with 11 units on it and when powered up the central control is not finding any units i would really like some help
Thanks

Crash Pilot
24-07-2010, 02:55 PM
You need to put in group numbers into each indoor unit. Once you do the first group number 88 will disappear.
You should start at group 1-00 for your first unit and then to 1-10 for your 11 indoor units.

Hold down test button for 4 seconds then timer up and down to set group numbers then press confirmation button once.(Depends on what controller you have)