20-07-2010, 07:44 PM
hello,can anybody help me out here?
i'm in iraq and having trouble with a 40ft freezer container. when i set the temp at -20 it shuts off on high discharge, but when set at -18, it works fine.
The temperture here in iraq reach at 140f, could this unit just be working to hard to reach temp..

cadwaladr
20-07-2010, 10:39 PM
clean the condensor with ofn or compressed air thats will help,how hot is the liquid line drier it should be warm in that ambient[the temperature of water you wash with]could be overcharged with gas ,whats its history?

ZoO
22-07-2010, 04:27 AM
What are the actual pressures at shut down?

The Fox
28-07-2010, 07:28 AM
are you sure the ambient you mentioned is correct?.
60*c !. we generally find units will run ok up to around 50*c, after that they start to struggle. seems odd it will run ok to -18 but will shutdown at -20 does not make much sence as you would expect all pressures to be dropping as you pull temp. down.
fit your gauges run and check pressures,water temp.ect.