View Full Version : lubricant oil in refrigeration system



Lc_shi
14-07-2010, 01:51 AM
Dear sirs

I know the importance of lubricant oil in refrigeration system ,the positive is to keep compressor in good state and the negative is to hinder the heat tranfer of heat exchanger due to the oil film.
The oil return is very important in the long pipe refrigeration system. How to manage the oil best in refrigeration system from design to installation ?
Who can offer clues at this issue.
Thanks in advance!

regards
LC

NoNickName
14-07-2010, 09:06 AM
It's easy: keep the oil in the compressor as much as possible.

toprunner
14-07-2010, 09:18 AM
You keep as high speed as possible in the tubes with respect to the pressure loss. The tricky part is the evaporator.

Lc_shi
19-07-2010, 01:09 AM
thanks ,
IT's right to keep the high enough speed but the big pressure loss is not good for the system efficiency.

Ernie
19-07-2010, 04:06 AM
You keep as high speed as possible in the tubes with respect to the pressure loss. The tricky part is the evaporator.


i read an article awhile ago which advised to stop adding oil trap's in a suction line on long vertical riser's. i believe it was in an HRAI update/magazine.

would it be to avoid the pressure loss in a trap?

thanks.

NoNickName
19-07-2010, 07:51 AM
I assume they suggest to use double risers instead of oil traps. Can you point us to the article, if it is available on line?

Brian_UK
19-07-2010, 10:26 PM
Sorry LC, missed your post earlier.

McQuay do a useful piping guide which may be of interest to you...
http://www.mcquay.com/mcquaybiz/literature/lit_systems/AppGuide/AG_31-011_120407.pdf

There is a good range of documents also available...
http://www.mcquay.com/McQuay/DesignSolutions/GreenWayPage3