PDA

View Full Version : fujitsu fault codes



andy1957
13-07-2010, 04:44 PM
Hi, I have a AOYR 12 LC system flasing twice on the timer led, any ideas

nike123
13-07-2010, 06:16 PM
Outdoor unit does not have timer led.:p
Your error code means that indoor unit doesn't receive communication signal from outdoor unit.

andy1957
13-07-2010, 06:53 PM
The timer led on the indoor unit is flashing twice. Chears

nike123
13-07-2010, 07:13 PM
The timer led on the indoor unit is flashing twice. Chears
Yes, but you gave us model number of outdoor unit.

bigor_2
14-07-2010, 09:32 AM
andy1957
1. Check cabel conection indoor<->outdoor units
2. Check fuse 20A on outdoor unit

andy1957
14-07-2010, 06:10 PM
found out that the fault is the out door board after talking with fujitsu tec dept. IE checked voltage on term 3 on the outdoor board the n tested it on the indoor board, both readings the same. \\\\going to remove the old system and fit a mitsi heavy inverter as i have had no trouble with them. Thanks to all