hi everyone,

can anyone give me some notes on how to properly installed a ref system piping. And for every ft or mtr how much loss are gone in the capacity of the compressor


thank you

Brian_UK
13-07-2010, 10:55 PM
Sorry, don't understand your question.

You state that you are a Refrigeration Designer and yet you are asking about basic things.

Refer to your text books.

lana
14-07-2010, 05:11 AM
Check Mcquay piping handbook.

Peter_1
14-07-2010, 08:00 AM
Sorry, don't understand your question.

You state that you are a Refrigeration Designer and yet you are asking about basic things.

Refer to your text books.

Yeah, but in country Earth, you can expect all kind of peoples :p

And for every ft or mtr how much loss are gone in the capacity of the compressor there's no loss gone in the compressor.
You have to calculate DP over the lines and translate this to your compr. cap.

lynark
15-07-2010, 04:31 PM
hi guys,

sorry for misleading question. actually i ones read from this site that your cooling capacity changes per 2F pipe loss = 100%, 4 F = 90 % and soon on or maybe i'm wrong thats why i want to read it again but can't seem to find it in the forum. i think its from dupont.

i just need some technical details for customer presentation. because right now we will be installing a 70 mtr vertical rise. and the allowable for compressor is 50 mtr with PTrap every 3 to 4 mtr. just need to gather more info.