new here , and trying everwhere to get help !!
we have a 3 phase compressor and a 2 fan single phase condensor , freezor unit
we need help wiring all this up through the defrost , to the stat wich is the a419 and condensor , selinoid and all
they did'nt send any wiring diagram with this stuff !!!
tecumsah compressor and not sure on the condensor model , really burnt out on this thing 12 hours on the roof today !!
not sure where i'm supossed to post or what ??

chillled
08-07-2010, 10:46 PM
Best to get an all in one controller such as a thermomax etc available from climate centre. As for power to compressor you need a control circuit and contactor, probably best getting someone experienced to take a look

frank
09-07-2010, 08:04 PM
Best to get an all in one controller such as a thermomax etc available from climate centre.
Are you sure? The OP is in the USA...... :)

dane mccarthy
01-08-2010, 11:52 PM
control the soleniod with your thermostat, and control the compressor on a LP switch, use a HP switch to control one of your condenser fans to control head pressure and the other condenser fan run with the compressor... if you need this drawn up let me know..

nike123
02-08-2010, 08:07 AM
new here , and trying everwhere to get help !!
we have a 3 phase compressor and a 2 fan single phase condensor , freezor unit
we need help wiring all this up through the defrost , to the stat wich is the a419 and condensor , selinoid and all
they did'nt send any wiring diagram with this stuff !!!
tecumsah compressor and not sure on the condensor model , really burnt out on this thing 12 hours on the roof today !!
not sure where i'm supossed to post or what ??


You need someone with knowledge in electrical automation to do that for you, since, from your questions, and result, you are not capable to do that, and electricity is not forgiving force.
Wiring diagram is not needed to experienced technician. It is simple, but if you are not familiar with that, you should let someone experienced to do that, and you look, ask and learn while he is doing it.

Correct section would be:
http://www.refrigeration-engineer.com/forums/forumdisplay.php?f=70

NoNickName
02-08-2010, 08:48 AM
control the soleniod with your thermostat, and control the compressor on a LP switch, use a HP switch to control one of your condenser fans to control head pressure and the other condenser fan run with the compressor... if you need this drawn up let me know..

Come on, this is technology of the 50s. No place for this setup in 2010.

http://www.dixell.com/linea58/download/XR06CX_GB.PDF is a starting point for a modern design of a condensing unit.

nike123
02-08-2010, 09:18 AM
Or something like this one:
http://www.pego.it/web/prodotti_dettaglio_eng.asp?l=1&p=49&s=3

multisync
02-08-2010, 09:32 AM
Come on, this is technology of the 50s. No place for this setup in 2010.

http://www.dixell.com/linea58/download/XR06CX_GB.PDF is a starting point for a modern design of a condensing unit.

What's the difference?

That controller will operate a sol valve and pump down the system exaclty how he suggested. He mentioned 'stat' but did not define what type of stat either..

Sure the head isn't going to be controlled as closely as a speed controller but that's all you can comment and that controller isn't applicable for that in any case...:D

NoNickName
02-08-2010, 10:10 AM
What's the difference?


Anti recycle, interlocks, probe management, display of readings and parameters, avoidance of repeated LP stops, defrost management (conditional starts, stops and dripping times), identification of alarms by code.... shall I continue?

multisync
02-08-2010, 12:47 PM
Anti recycle, interlocks, probe management, display of readings and parameters, avoidance of repeated LP stops, defrost management (conditional starts, stops and dripping times), identification of alarms by code.... shall I continue?


You could add dodgy Italian electronics but that would be cruel and totally untrue..

However you are still not giving the guy the benefit of the doubt as he just said 'stat' and that could mean all manner of things including an all singing all dancing electronic controller...

NoNickName
02-08-2010, 03:52 PM
It's nice to see that the scepter of the most chauvinist nationals in Europe is no longer in the hands of French.
To be completely honest, I was one of the first to adopt Trend in Italy, and alas soon reverted back to the dodgy Italian controllers.
It would need lots more fish and chips for British electronics to be that dodgy, my friend.
And no, a mechanical thermostat is well removed from the digital regulator I suggested, but if you don't get the difference, you can still keep using the bits and pieces you are familiar with.

bill1983
04-08-2010, 09:03 PM
do you mean reliability, interchangability, simplicity, adaptability. all those parts that we all once loved?
chauvanistic? non!
realistic but simplistic? prego

NoNickName
04-08-2010, 09:31 PM
Do you mean modern, dependable, flexible and efficient?

Or do you mean old fashioned, legacy, energy hungry? PRONTO!

bill1983
05-08-2010, 07:20 PM
nice come back!
no, what i meant was simple to understand and learn from if labour intensive to install. if the guy is capable, and just lacks understanding why not give him something he can do.
everything can be explained using the terminology of a light switch. and lets face it, if he can't understand that then Nike is right, he needs experienced help before he attempts a simple to install, but slightly more complicated to understand all-in-one.
what's the weather like over there?

mikeref
05-09-2010, 11:59 PM
control the soleniod with your thermostat, and control the compressor on a LP switch, use a HP switch to control one of your condenser fans to control head pressure and the other condenser fan run with the compressor... if you need this drawn up let me know..
Simple and easy to set up. Thats how i would have replied to this thread. One can always move onto more complex control equipment when or if they wish to