How can I calculate the pipe weight? Is the diameter of the pipe is 1100mm.
lawrence1
03-07-2010, 04:50 AM
That's one big suction line.
nr1990
03-07-2010, 05:04 AM
its a storage pipe tank or somthing...
icecube51
03-07-2010, 06:26 AM
use the same formula as for a pipe of 3/8" or 1/2" and so on.
what is it you want to now? the inner volume per meter of gas or liquid?
the amount of gas/liquid thats going throu the pipe per second?
define youre question so whe are able to help you out.
Ice
sterl
03-07-2010, 02:23 PM
Empty pipe:
pi*d*t times density of the material...watch your units!
Volume of contents: pi*d*d/4*length
To work the weight of the contents: you need to know its density at the highest pressure you can expect; and if that implies it could be both liquid and gas (refrigerant in cold surroundings;; pumped recirc arrangement or ?) you will have to figure how much of the frig charge could reasonably end up in this pipe....