hi everybody
im new in this forum
im having e problem with e rhoss chiller CWA\E 70
here is the situation . the unit has 4 compressors and only 2 are running and on display gives E 22 error
anyone any idea what s going wrong
thanks in advance ;)

David40
01-07-2010, 04:52 PM
I'd start with the basics. Manufacturer data should tell you what error 22 might indicate, then check those first. Next I'd check for voltages at the contactor and contactor coils.

icecube51
02-07-2010, 05:46 AM
check for high or low pressure on that circuit.

Ice

iceman zl
03-07-2010, 08:54 PM
thank you guys for your suggestions i really appreciate this but i think im gonna need e rhoss manual for cwa/e 70 model . has it anybody
thanks again :o

frode74
05-09-2011, 12:30 PM
Low pressure circuit 2

Peter_1
06-09-2011, 10:38 AM
Indeed LP for Circuit 2 and you need to switch off power to the controller to reset this.
Lack of gas (don't overcharge because there's no receiver) or lack of load or TEV fault.