I have a second hand old evaporator but there is no label about capacity of this evaporator. How can I calculate the capacity of this evaporator..." it used in -30 C room"

Thanks...

chemi-cool
25-06-2010, 01:07 PM
What is the compressor make and model?

You can get a lot of info from it.

Also check the TXV for capacity at this temp.

And what refrigerant are you using.

scorpx
25-06-2010, 01:25 PM
R22 is the refrigerant.
I will send you compressor model later.
What is TXV ?

Is there any another way to understand capatiy of evaporater.

Some of my friend can calculate approximate capacity of evaporater with multiply hight and with of evaporater and some other mesurmets.

scorpx
25-06-2010, 01:40 PM
compressor is BITZER 6G

chemi-cool
25-06-2010, 04:08 PM
TXV = Thermostatic Expansion Valve.

By using rule of thumb, if evaporator is made of 5\8 pipe, 15 meters for 1 ton refrigeration. [TR]

Bitzer 6G-30.2 will give you at 40°C condensing temp, -35°C evaporating temp --- 24.1 KW = 7 TR

abet_meneses
26-06-2010, 03:07 PM
give us the ff evap coil specs.pipe size,rows.tube phase and fin length.