PDA

View Full Version : Pump Alignment



cspenard
24-06-2010, 01:25 AM
In the next week I am going to have to align the 3 chilled water pumps for the new Trane screws my company just installed. Problem is, it's been ages since I've done one and I want to do it the correct way, not just use a straight edge. My company also doesn't have 5K to drop on a laser tool, so any advice or direction to a good alignment website would be appreciated.

NH3LVR
24-06-2010, 02:27 AM
Laser tool not needed! A dial indicator does well.
Look up this link and it will tell you all you need to know.
http://www.carlylecompressor.com/Files/Carlyle_Compressor/Local/US-en/documents/039-185_5FHShaftAlignment_lowres.pdf

Tesla
24-06-2010, 05:00 AM
Thanks NH3LVR
I d.loaded and checked it out and it's a goodie.

Gingerair
24-06-2010, 10:10 PM
Great book, thanks NH3LVR..

glenn1340
25-06-2010, 07:44 PM
Great reference book, thanks very much.

Tycho
25-06-2010, 11:09 PM
Very nice NH3LVR!


But a small tip, always ALWAYS! allign the machine sideways before you check the height.

if the machine is off sideways, they height will be off as well.

When I align machines, the first thing I do is make them parallel, even if they are off center.

when they are parallel I move the motor sideways and try to keep it within the parallel as I move it sideways.


Once you have the motor clocked in within the sideways tolerance you can start worrying about the height.

cspenard
26-06-2010, 01:17 PM
Thanks for the advice and thanks for the link NH3LVR it's very much appreciated.