17-06-2010, 07:22 PM
hi
i have 2 x downflows which are on a duty/standby set up, is there a way to make each unit run independantly...i have tried to disconnect the comms but the unit goes into alarm.

these units a r22 system wit a controller wit up down and enter button...

any ideas

rgrds phil

moondawn
17-06-2010, 07:41 PM
hi there could you isolate one of them so the standy by unit comes on.

cheers lee

Grizzly
17-06-2010, 08:23 PM
Hi Phil.
"You got mail"
Check out software level 3
Auto sequence - Stand Alone.
Grizzly

philjd26
20-06-2010, 05:06 PM
Hi Phil.
"You got mail"
Check out software level 3
Auto sequence - Stand Alone.
Grizzly


got that thanks alot grizzly.

rgds phil