16-06-2010, 10:50 PM
Hey guys,
Hope someone can help.
I have 2x PUHY-P300YHM-A piped together, with four indoors (havent checked models yet). No BC .The problem is no cooling performance at indoors. Its an open plan retail area with another system identical to this one,the two outdoors on this other system are running flat out all day so the demand is there.
On the system im working on one outdoor will run at about 40Hz for about 10 mins then the second one will kick in and run at the same for about 5-10 mins and then stop. The first unit will continue running after this. Some points to mention;
-Frost coming back on suction, and on receiver.
-Liquid line cold.
-No heat in condenser coil.
-Tc of -13
-Discharge temp can hover around 50 and get as high as 70
-HP between 18- 30 bar (was at 35 at one stage)
-LP around 5 bar ,,,,SOG???? Maybe not
-Very important,,,the indoor units are doing nothing, no temp difference between inlet and outlet on any of the units
I thought maybe one of the units was passing gas with LEV stuck open, this would account for frosting suction. But surely the unit that was passing would show some cooling performance while starving the other units. And yet with a cold liquid line and frosting suction line its as if the indoor units arnt connected to anything. (the pipes are connected and to the right outdoor).
When i got to this site at first i thought poor performance, inverters not ramping up, SOG, had no recovery machine with me to verify the charge so i decide to add a kg to see if it made a difference, none , i added another 4 kg to see and still nothing. I believe these units can take up to 5kg overcharge without effecting system. However then i got a 1500 fault, excellent, making things difficult for myself as usual. Im going back to site in morning and the first thing im gonna do is verify the charge by weight and get that out of the way.I was wondering if anyone had any other ideas on what the underlying issue is, whats stopping the comp running above 40Hz, why is there no temp difference at indoors?
I did read a post by Pie Man regarding the same 1500 fault and got some helpful tips on Discharge superheat and its effect on comp.
I did check actual and real readings for HP and Discharge temp on one unit but not the other.
Any readings ive got are from SW-1, i was meant to organise a site visit with ME for maintenance tool a while ago but with 16 hour days becoming the norm ive let it slip.
I look forward to the time when i can offer advice instead of receiving it.
Regards
Hope someone can help.
I have 2x PUHY-P300YHM-A piped together, with four indoors (havent checked models yet). No BC .The problem is no cooling performance at indoors. Its an open plan retail area with another system identical to this one,the two outdoors on this other system are running flat out all day so the demand is there.
On the system im working on one outdoor will run at about 40Hz for about 10 mins then the second one will kick in and run at the same for about 5-10 mins and then stop. The first unit will continue running after this. Some points to mention;
-Frost coming back on suction, and on receiver.
-Liquid line cold.
-No heat in condenser coil.
-Tc of -13
-Discharge temp can hover around 50 and get as high as 70
-HP between 18- 30 bar (was at 35 at one stage)
-LP around 5 bar ,,,,SOG???? Maybe not
-Very important,,,the indoor units are doing nothing, no temp difference between inlet and outlet on any of the units
I thought maybe one of the units was passing gas with LEV stuck open, this would account for frosting suction. But surely the unit that was passing would show some cooling performance while starving the other units. And yet with a cold liquid line and frosting suction line its as if the indoor units arnt connected to anything. (the pipes are connected and to the right outdoor).
When i got to this site at first i thought poor performance, inverters not ramping up, SOG, had no recovery machine with me to verify the charge so i decide to add a kg to see if it made a difference, none , i added another 4 kg to see and still nothing. I believe these units can take up to 5kg overcharge without effecting system. However then i got a 1500 fault, excellent, making things difficult for myself as usual. Im going back to site in morning and the first thing im gonna do is verify the charge by weight and get that out of the way.I was wondering if anyone had any other ideas on what the underlying issue is, whats stopping the comp running above 40Hz, why is there no temp difference at indoors?
I did read a post by Pie Man regarding the same 1500 fault and got some helpful tips on Discharge superheat and its effect on comp.
I did check actual and real readings for HP and Discharge temp on one unit but not the other.
Any readings ive got are from SW-1, i was meant to organise a site visit with ME for maintenance tool a while ago but with 16 hour days becoming the norm ive let it slip.
I look forward to the time when i can offer advice instead of receiving it.