Pawel_Wisnik
15-06-2010, 01:43 PM
Dear all, placing condenser with liquid receiver below compressor (~5 meters below) cause that installation does not function? Could you give me theoretical background concernig that issue please?

Regards

Pawel

Brian_UK
15-06-2010, 11:30 PM
What does not function in your set up?

lana
16-06-2010, 03:49 AM
Hi there,

Most probably you have a problem with liquid line which goes up 5m. You have to calculate the correct liquid line size and also required sub cooling so that a solid liquid line reaches the TEV.

Cheers

Pawel_Wisnik
16-06-2010, 06:41 AM
Thx for expl.
Brg Pawe.

Peter_1
16-06-2010, 09:16 AM
Dear all, placing condenser with liquid receiver below compressor (~5 meters below) cause that installation does not function? Could you give me theoretical background concernig that issue please?

Regards

Pawel

I don't see any problem with this setup.
But what IS your problem exactly?

icecube51
16-06-2010, 09:14 PM
probably a low pressure problem on the LP inlet of the compressor..... i think?

Ice

Pawel_Wisnik
17-06-2010, 06:25 AM
I don't see any problem with this setup.
But what IS your problem exactly?

Hi Peter,

I am forced to apply such layout in one of my sites within a couple a weeks to come, but in the meantime I heard an opinion that such setup did not work at all (but without explanation why it did not and what was the main problem), in my opinion there is no threats in it, but just to be sure I also dropped post here to see opinion from you, opinions that I appreciate very much .

Regards

Pawel

Graham
17-06-2010, 06:54 AM
Possible accumulation of oil in receiver?

Peter_1
17-06-2010, 07:00 AM
Make sure your line going up is large enough in diameter and if you want to use EEV's on your evaporators, try to install a subcooler (PHE) after your receiver.

Aik
17-06-2010, 12:52 PM
Hi Peter,

I am forced to apply such layout in one of my sites within a couple a weeks to come, but in the meantime I heard an opinion that such setup did not work at all (but without explanation why it did not and what was the main problem), in my opinion there is no threats in it, but just to be sure I also dropped post here to see opinion from you, opinions that I appreciate very much .

Regards

Pawel
May be it was a case when compressor above condencer and receiver near the compressor (above condencer)?

icecube51
17-06-2010, 05:02 PM
i am more thinking in the line of the compressor. problems whit the oil return. i don't think there was a refrig mensioned in this topic.

Ice

benijoseph
17-06-2010, 06:42 PM
It should work, If it is not working give the pressure reading of LP and HP?

RGDs

Scramjetman
17-06-2010, 11:47 PM
Provided the line size is right, it should work ok. Oil return can be a problem in condensers lower than the compressor particularly if the ambient conditions are low and head pressure control is poor. It often turns turns to sludge and sits in it occupying condenser area. Then a young tech comes along - sees no oil in the compressor and promptly adds another litre or two which also ends up in the condenser and so on it goes.

Best plan is to probably think about an oil separator to take care of the oil issues, make sure the lquid line has a low enough pressure drop and it should work fine.

Pawel_Wisnik
18-06-2010, 07:34 AM
Make sure your line going up is large enough in diameter and if you want to use EEV's on your evaporators, try to install a subcooler (PHE) after your receiver.

Hi Peter,
I do so

Regards
Pawel

Pawel_Wisnik
18-06-2010, 07:59 AM
i am more thinking in the line of the compressor. problems whit the oil return. i don't think there was a refrig mensioned in this topic.

Ice

Hi,
in my opnion there should not be a problem with oil, it flows freely down to condeser via discharge line then within condenser and liquid receiver dissolves in refrigerant.

Peter_1
18-06-2010, 08:03 AM
Indeed, you will not face oil problems and surely not in the discharge and liquid lines. Liquid will fush out all the oil

Aik
18-06-2010, 09:58 AM
In my opinion there is one problem of your system.
On summer ambient temperature may be high then room temperature where compressor situated. If compressor stop long time then its temperature may be smaller then condencer (and receiver). And refrigerant may migrate from receiver through condencer to head of compressor and condense there. When compressor start then may be hydraulic shock...

icecube51
18-06-2010, 09:15 PM
always safe to mount an oiltrap evry 3mtr.

Ice

Peter_1
18-06-2010, 09:49 PM
In upgoing liquid lines and flowing down discharge lines? :confused:

Gingerair
18-06-2010, 11:27 PM
A non-return valve in the liquid line outlet from the condenser would not be a bad idea...

icecube51
19-06-2010, 05:57 AM
in this case Peter, upgoing.

Ice

nike123
19-06-2010, 06:47 AM
http://i49.tinypic.com/ejg3mh.jpg
.........................

Pawel_Wisnik
19-06-2010, 10:45 PM
In my opinion there is one problem of your system.
On summer ambient temperature may be high then room temperature where compressor situated. If compressor stop long time then its temperature may be smaller then condencer (and receiver). And refrigerant may migrate from receiver through condencer to head of compressor and condense there. When compressor start then may be hydraulic shock...

Hi
in this case machniery room always is at equal or a bit higher temperature than ambient, even in summer time.

Peter_1
20-06-2010, 10:12 AM
An NRV will give you an additional DP in your liquid line and decrease overall system performance.
Why you need it anyhow? What is its benefit?

Aik
21-06-2010, 06:42 AM
When compressor stop, if temperature of condencer and receiver will bigger than compressor, than refrigerant in liquid phase will evaporate in condencer and condence near more cold compressor (migrate).


Hi
in this case machniery room always is at equal or a bit higher temperature than ambient, even in summer time.
Then I don't see problems in your system...

Aik
21-06-2010, 11:28 AM
A non-return valve in the liquid line outlet from the condenser would not be a bad idea...
In this system it would be better install check valve in the gas line on inlet to the condencer.


always safe to mount an oiltrap evry 3mtr.
Oiltraps don't stop migration...

icecube51
21-06-2010, 04:17 PM
Oiltraps don't stop migration...

but whit the migration of the refrig, some oil will return, so the compressor will always have some oil to work whit.

Ice

nike123
21-06-2010, 04:49 PM
I don't see any problem except that subcooling must be enough to compensate for 0,63 bar pressure drop due to liquid column of liquid refrigerant in 5 m pipe.
Oil is not of any concern if it is soluble with liquid refrigerant.

Aik
22-06-2010, 06:31 AM
but whit the migration of the refrig, some oil will return, so the compressor will always have some oil to work whit.

Ice

In any case in Pawel_Wisnik's system oil trapes don't need on discharge line.


I don't see any problem except that subcooling must be enough to compensate for 0,63 bar pressure drop due to liquid column of liquid refrigerant in 5 m pipe.
Oil is not of any concern if it is soluble with liquid refrigerant.
I have the same opinion...

Peter_1
22-06-2010, 12:06 PM
http://i49.tinypic.com/ejg3mh.jpg
.........................

In the Suva example, gas line, 33.9 psi at bottom and 34.1 psi at the top :eek:

nike123
22-06-2010, 04:45 PM
................................
Deleted!;)
You are right, it is mistake.

Peter_1
22-06-2010, 08:47 PM
Why then the bottom weights less?

nike123
22-06-2010, 09:09 PM
I think you misunderstand my last post. Deleted is my comment (which is wrong) that everything is OK on that Suva picture, because i did not paying attention at what is bottom and what is up.
Than I confirmed that you are right.

garethjones10
24-06-2010, 01:24 PM
Hi

This is Gareth Jones

Most probably you have a problem with liquid line which goes up 5m. You have to calculate the correct liquid line size and also required sub cooling so that a solid liquid line reaches the TEV.

Regards,

Gareth
CNM ONLINE

garethjones10
25-06-2010, 09:59 AM
Hi

Most probably you have a problem with liquid line which goes up 5m. You have to calculate the correct liquid line size and also required sub cooling so that a solid liquid line reaches the TEV.

Regards,

Gareth
CNM ONLINE