View Full Version : System requirements changing from R-22 to R-410A



sanjay261289
08-06-2010, 05:39 AM
I have to design a new system using refrigerant R-410A instead of using R-22

What would be the changes required???

Plz even if you show me the right path i may be able to follow and get solution...

Plz sir help me!!!

I have to operate between temperature limits of 45 degree celsius (condenser) and 2 degree celsius (evaporator).

Any type of help would be grateful

Thanks in advance

Brian_UK
08-06-2010, 11:43 PM
Have you already designed an R22 unit ?

sanjay261289
09-06-2010, 05:36 AM
Have you already designed an R22 unit ?
we were using R-22 unit for many years (5-8)

Brian_UK
09-06-2010, 11:34 PM
Use the appropriate components suitable for the higher pressures.

sendhilkmar
10-06-2010, 01:30 PM
Tube Size could be one step lower than R22 but wall thickness should be higher.

sanjay261289
11-06-2010, 07:53 AM
Tube Size could be one step lower than R22 but wall thickness should be higher.
sendhilkmar,

thanks for the info.

i know that the system pressures of r-410A is 50-60% higher than the R-22 and its latent heat capacity is also higher than r-22 because of which u gave me that suggestion.

But instead of using a thicker and smaller dia pipe for connections if i use the thinner ones but of larger dia. will it pose me any difficulty???

waiting for reply

thanks in advance!!!!

Brian_UK
11-06-2010, 11:44 PM
Pipe must be suitable for the refrigerant being used regardless of size.

What sort of systems are you designing?

sanjay261289
12-06-2010, 10:21 AM
Pipe must be suitable for the refrigerant being used regardless of size.

What sort of systems are you designing?
water chiller

rickyccong
13-06-2010, 08:34 AM
Recently I have inspected by Eddy Current Tubing Examination on "York" Chiller Mode: YSCBCAS35CD D on the Condenser and Evaporator Enhanced Copper tube.
The Evaporator tube size OD 3/4" diam x 1.75 mm wall thickness and under the fins wall thickness 1.25 mm wall thickness.
The Condenser tube size OD 3/4" diam x 2.11 mm wall thickness and under the fins wall thickness 1.5 mm wall thickness.
The refrigerator use 132b.
Hope this will help you on the design.

moideen
13-06-2010, 11:31 AM
Recently I have inspected by Eddy Current Tubing Examination on "York" Chiller Mode: YSCBCAS35CD D on the Condenser and Evaporator Enhanced Copper tube.
The Evaporator tube size OD 3/4" diam x 1.75 mm wall thickness and under the fins wall thickness 1.25 mm wall thickness.
The Condenser tube size OD 3/4" diam x 2.11 mm wall thickness and under the fins wall thickness 1.5 mm wall thickness.
The refrigerator use 132b.
Hope this will help you on the design.
can you please explain eddycurrent test method.:cool:
moideen

sanjay261289
14-06-2010, 11:23 AM
Recently I have inspected by Eddy Current Tubing Examination on "York" Chiller Mode: YSCBCAS35CD D on the Condenser and Evaporator Enhanced Copper tube.
The Evaporator tube size OD 3/4" diam x 1.75 mm wall thickness and under the fins wall thickness 1.25 mm wall thickness.
The Condenser tube size OD 3/4" diam x 2.11 mm wall thickness and under the fins wall thickness 1.5 mm wall thickness.
The refrigerator use 132b.
Hope this will help you on the design.
Thank u for ur info