PDA

View Full Version : Ice build up on the air conditioning high side



hotrodinvi
05-06-2010, 03:50 AM
hi
just had a samsug mini split installed. worked fine for about 2 days. when i turned on the unit for about 5 minutes i noticed that it was only blowing hot air, when i check the out side unit the small copper line was covered in ice the bigger copper line was warm. i turned the unit off for about 10 minutes and then on again it did the same thing. what could be causing this problem.
thanks for your help

ironmen
05-06-2010, 05:30 AM
system is undercharge ckeck for leakage.check for trace of oil on the tail.between evap and condenser pipework.and all flarenut.All the best.

monkey spanners
05-06-2010, 04:16 PM
Get the installers back to check it over.

hotrodinvi
05-06-2010, 07:30 PM
Thank you I checked it and there is a leak thank you