Hi we have onboard a ship a RefComp waterchiller.

It is a RefComp SRC-S 305 (2 x screw compressors)

We just made oil/filterchange on it and now we can not start again.

We hav following alarms and we can not reset.

48 L1 Probe fail
48 L2 Probe fail
48 H1 Probe fail
48 H2 Probe fail

While we were changing the oil/filters we had the power breaker off.

Now after we put the breaker on we have these alarms.

How can we get this Refcomp up and running again ?

From Daniel....

hyperion
03-06-2010, 01:04 PM
There is probably an alarm reset in the control panel, or you may have to access the maintenance program to allow you to reset these.

ptsac
03-06-2010, 09:24 PM
Hi we have onboard a ship a RefComp waterchiller.

It is a RefComp SRC-S 305 (2 x screw compressors)

We just made oil/filterchange on it and now we can not start again.

We hav following alarms and we can not reset.

48 L1 Probe fail
48 L2 Probe fail
48 H1 Probe fail
48 H2 Probe fail

While we were changing the oil/filters we had the power breaker off.

Now after we put the breaker on we have these alarms.

How can we get this Refcomp up and running again ?

From Daniel....


The lp and hp transducers are not seeing any pressure, open the liquid solenoids briefly to get pressure up to 1 bar and alarm 48 should go.

Challenger
04-06-2010, 06:49 AM
I have it up and running now.

It was impossible to manual reset these alarms. According to the manual the alarms has automatic reset.

The suction and discharge valve was fully open, but i still had the alarms.

Then i connected a small hose from the lubeoil filling valve to a service valve just before the thermostatic exp valve. I let in a little pressure to the compressure via the oil filling valve and then the alarms disappered.

After that I was eable to start without any problems. Its running fine now..

Bye bye.

Daniel

mbadanai
04-06-2010, 01:53 PM
Here's a bit of history and contacts if you need them.

RefComp and Thermokey form together the RTH group which is an independent group which has one owner who is the original founder Mr. Candio.
RefComp makes the very same screw and piston compressors at their factories both near Vicenza in Italy and in Shanghai in China while Thermokey makes many types of heat exchangers for Air Con, Refrigeration , Process Control, Close Control , Power and Energy and Solar Energy markets and manufactures in Italy , China and Brazil.

About 30 years ago Mr. Candio used to own Artec (heat exchangers) which he after sold to Alfa Laval. After RefComp was then founded and was a pioneering company with screw compressor technology specifically designed for HVAC and Refrigeration applications. During this past century Bitzer used to sell the large RefComp screw compressors through their sales network because back then they did not manufacture yet this kind of new screw compressor.
After Thermokey was then founded. Nowdays Thermokey is pioneering in large aluminium microhannel heat exchangers specifically designed for HVAC and Refrigeration applications

you can contact them at :

sales@refcomp.it
sales@thermokey.it