02-06-2010, 07:50 AM
Hi All,

Is it possible to convert an existing CFC refrigerant coil to water chiller coil......i.e, water through tube rather than R404A refrigerant?

Any thoughts/suggestions?

regards

Brian_UK
02-06-2010, 11:54 PM
Clean the oil from the tubes and you can run what you like through, just don't change your mind and try to go back to refrigerant. ;)

The duty will probably change though.

goshen
03-06-2010, 05:01 AM
Clean the oil from the tubes and you can run what you like through, just don't change your mind and try to go back to refrigerant. ;)

The duty will probably change though.

Hi
as said this might be possible, but your pressure drop will be entirley different, this could cause problems!:)
i dont think i would start an adventure like this!

GBRD
03-06-2010, 07:01 AM
thats a good point Goshen........any other thoughts of small modifications on U-bends to the circuit etc ........?

cheers

TXiceman
23-10-2010, 02:07 AM
A DX coil will have a distributor and/or orifice plus circuiting for refrigerants. A coil circuited for water will be different.

Ken