01-06-2010, 10:22 PM
I've been called to shoot a freezer. I was supposed to replace a bad compressor but was called of to another location so another replaced the Copeland that I gave him. Now I've had to go back and I replaced the starting components relay, start cap and run cap. The compressor still won't start most of the time, I start with 213v and go down to 198 or so when it tries to start I switched panel boxes, breakers and wiring to the unit same result. I have a draw of 48 amp when it tries and won't start. Any help or ideas appreciated.

Brian_UK
01-06-2010, 10:45 PM
Sounds like you may have a voltage supply problem. Can you check the voltage at the site source when the compressor starts?

AlwaysLearning
02-06-2010, 12:31 AM
The voltage drops but not as bad at the panel box

tbirdtbird
02-06-2010, 01:16 AM
213 VAC Open circuit voltage seems low to begin with. Also check for bad connections and undersized wire. What is the amp rating on the comp? What size branch circuit wiring? How far away is comp from service?

dirk
02-06-2010, 01:21 AM
sounds like you have loose connections starting gear failure or the compressor is damadged did the installer try to start the unit with the original stating kit.

AlwaysLearning
02-06-2010, 01:22 AM
The compressor is about 25 feet from service, branch circuit wire is 6 gauge, I did see 14 gauge from the end of the branch to the defrost timer and to the compressor but it ran fine before they say

dirk
02-06-2010, 01:22 AM
Sorry tbird you beat me to it.

AlwaysLearning
02-06-2010, 01:32 AM
The installer didn't change relay or either of the caps, don't know why that's why that was the first thing that I did. It ran with the old gear for 4 days

dirk
02-06-2010, 02:37 AM
If possible through a correctly rated extension and protected circuit take supply from another circuit to unit. If unit runs problem solved. if not first check compressor then bypass all switching gear in line to compressor one by one, this is the long route but you will eventually find fault.

tbirdtbird
02-06-2010, 02:52 AM
The only thing I'd run off 14 ga is an electric toothbrush

dirk
02-06-2010, 03:24 AM
14ga is not only good for toothbrushes, domestic speakers also do well on it.

ref717
02-06-2010, 07:57 PM
Pls. give more details on your system.,what is the HP/KW rating of your compressor?.,the capacitors rating?.,is it a hermetic compressor?..