PDA

View Full Version : Cleaning tubes in Shell and tube condenser



Harbour View
31-05-2010, 04:43 AM
Does anyone know the procedure to clean the copper tubes of a shell and tube water cooled heat exchanger?
what cleaning agents should I use?

lana
31-05-2010, 05:41 AM
Hi there,

The cleaning agent is Hydrochloric Acid with 10% concentration.
Commercial de-scaling agents usually contain corrosion inhibiting agents.
Be careful, copper inhibiting agents are very corrosive with galvanized steel. Separate the copper pipework from the steel piping.
You have to use a tank with a pump and circulate the solution through the condenser. When de-scaling is complete then circulate some kind of alkaline solution to neutralize the acid. After that circulate water to clean the remaining residue.
Cheers

Harbour View
31-05-2010, 10:50 PM
Thank you lana.