25-05-2010, 06:24 AM
Hi,
Could anyone help me with air con sizing problem please?
I am looking at 55 m3 microbiological laboratory with expected 10 ACH. There is one incubator running at 37 C 24 hrs a day and two equipment with combined power rating of 4 kW. Four persons are expected to work in the room. Worst outside air / ambient condition is 35 C at 85% RH and inside air hopefully can reach 23 C.
My calculation attempt:
- Ventilation load = ~41,000 kJ/h (72.09 kg.min/h.m3 * CMM * delta enthalpy) = 11 kW
- Load from people = 6 * 600 BTU = 3,600 BTU = ~3,800 kJ/h = ~1.1 kW
- Equipment load = ~6 kW
If I were to lump heat gain from envelope and miscellaneous item within 20% extra point, I end up with ~22 kW cooling load requirement.
Could any kind soul help confirm, feedback or correct my calculation and assumption here please?
Appreciate any help that can be given.
Thanks.
Could anyone help me with air con sizing problem please?
I am looking at 55 m3 microbiological laboratory with expected 10 ACH. There is one incubator running at 37 C 24 hrs a day and two equipment with combined power rating of 4 kW. Four persons are expected to work in the room. Worst outside air / ambient condition is 35 C at 85% RH and inside air hopefully can reach 23 C.
My calculation attempt:
- Ventilation load = ~41,000 kJ/h (72.09 kg.min/h.m3 * CMM * delta enthalpy) = 11 kW
- Load from people = 6 * 600 BTU = 3,600 BTU = ~3,800 kJ/h = ~1.1 kW
- Equipment load = ~6 kW
If I were to lump heat gain from envelope and miscellaneous item within 20% extra point, I end up with ~22 kW cooling load requirement.
Could any kind soul help confirm, feedback or correct my calculation and assumption here please?
Appreciate any help that can be given.
Thanks.