19-05-2010, 08:00 AM
I was leak testing yesterday when I noticed the pipework between the drier and the TEV on circuit 1 on this chiller was cold 11deg c. (It was shut down). Looking in the sight glass you can see the refrigerant flashing off.
Static pressures were
CCT 1 LP 3.14 bar HP 3.1
CCT 2 LP 3.0 HP 6.9
Now is this caused by the pressures equalising accross the TEV when the plant is shut down or is this circuit leaking after the TEV? I have been unable to find a leak so far.