confirm the calc

beer 5000 Litres

needs to cool from 25>10 = 15TD
time allowed =48 hours (max)

We made that around 15kw chiller

sneep
18-05-2010, 05:51 PM
Guy's

confirm the calc

beer 5000 Litres

needs to cool from 25>10 = 15TD
time allowed =48 hours (max)

We made that around 15kw chiller

1321 gal x 8.4 lbs = 11,096lbs x 27fdegrees = 299,592 btu's /48 =6,242
or 12,484 in 24hours.
6,242/3413kw= 1.82kw or 3.657kw in 24hrs.
Are you counting the walkin?

Aik
18-05-2010, 06:00 PM
1321 gal x 8.4 lbs = 11,096lbs x 27fdegrees = 299,592 btu's /48 =6,242
or 12,484 in 24hours.
6,242/3413kw= 1.82kw or 3.657kw in 24hrs.
Are you counting the walkin?
sneep's calculation is correct.