PDA

View Full Version : McQuay Chiller help.



sean
14-05-2010, 08:55 AM
Hi folks,

One of our guys needs some info regarding the capacity for a McQuay centrifugal chiller he is working on, any McQuay guys out there that can help us out would be much appreciated..thanks..

Model # PEH-087.E2417.2
Refrigerant R134A
LCHWT = 6DegC
RCHWT = 12DegC

ECWT = 22DegC
LCWT = 28DegC

Brian_UK
14-05-2010, 07:59 PM
As far as I can see from the McQuay site it is 350-600 tons.

Product manual here..
http://www.mcquay.com/mcquaybiz/literature/lit_ch_wc/Catalogs/pmpehpfh-1.pdf

they also have ops manual on the site.

ptsac
14-05-2010, 08:56 PM
Ther are many vessel, and gear code options for the same model compressor so Shop order or style number would need to be referred to McQuay.

However do you know what the chilled water flow rate is in l/s.
6 x 4.19 x l/s = kw

sean
17-05-2010, 03:04 PM
Thanks for the reply Brian i have sent him on the manual from your post so im just waiting on him to get back to me
Once again guys thanks very much for your invaluable help.......