I got a YORK air conditioner (2 year old) model YJCA-YJHA R22 (50 Hz), which refuse to start his condensing unit/compressor... no more cooling... after 2 mins the temperature display panel of the air cooler shows "F6". I got explanation from the Installation & Owner's manual.

Thanks in advance for your help & time.

Regards,

Grizzly
12-05-2010, 09:01 PM
Hi everyone,

I got a YORK air conditioner (2 year old) model YJCA-YJHA R22 (50 Hz), which refuse to start his condensing unit/compressor... no more cooling... after 2 mins the temperature display panel of the air cooler shows "F6". I got explanation from the Installation & Owner's manual.

Thanks in advance for your help & time.

Regards,

Hi Jean.
Welcome to the forum.
Please refer to the attached pdf.
You will see that fault F6 refers to( PG motor fault).
This is the Fan Motor.
Cheers Grizzly

Jean
13-05-2010, 04:08 AM
Hi Grizzly, Thanks for your quick reply and attached document, much appreciated.

Is it the fan motor of the indoor or outdoor unit which is faulty?

BR,

Grizzly
13-05-2010, 06:37 AM
Indoor.
Grizzly

cadillackid
13-05-2010, 09:36 AM
often it is the RPM sensor of the fan motor that causes these faults in splits... sometimes also you will find dirty contacts on the connectors going to the fan motor or if the filters have been left to get clogged the fan will spin up too quickly and issue a fault to the controller...

make sure the filters and coils are clear of any debris and that the fan wheel can spin freely..
-Christopher

Jean
15-05-2010, 06:14 AM
Hi Christopher,

Thanks for replying.

I found the indoor fan badly clogged with dirt, filters were ok. I dismantled the CPU + AC motor, cleaned the fan throughout.

Before putting back everything together, I am now testing the AC motor (not coupled to fan) but no spin so far... I check for voltage on the motor pins (Black-White & Black-Red got 210V).

Not sure how to test the grey-yellow-brown small wires which should be for speed control I presume.

Remote control and other electronic such as relay seem ok.

Where is this RPM sensor? how to test it?

PS: I attached a pic of the AC motor and CPU card if it can help...

3517

3518

Regards,
JMM

DiveTech
31-05-2010, 08:43 AM
I have the same problem with mine. I pulled the front panel off the evaporator and hit the little black reset switch on the circuit board. Fan then started to work, fan on condenser also came on but compressor isn't starting up. Its shot. Might be worth checking your compressor Jean.

semsem10001000
29-08-2010, 01:50 PM
what are the meanigs of
E1
E2
E3
E4
E5

Yuri B.
29-08-2010, 07:03 PM
Hello
I also was asking one day for York fault codes and somebody posted me this info (repost it for you as it has been):


Temperature Sensor Resistance Readings
Temperature 0C 10C 20C 30C
K Ohms 35K 20K 13K 8K

Fault Codes for RAHC, YKHC & YUHC Models
Indoor lights
Operation Timer Defrost
Flash Flash Flash Outdoor Problem
Flash ID Air Sensor Fail
Flash ID Pipe Sensor Fail
Flash OD Pipe Sensor Fail
Flash Flash PCB Fail


Outdoor LEDS 3ph models only
LED1 LED2 LED3
Flash Off Off Phase Error
Flash Flash Off Pressure Switch
Off Off Flash Overcurrent
Off Flash Flash OD Pipe Sensor
Off Flash Off OD Air Sensor
Flash Flash Flash Hi Temp Protection

HVHC Inverter Fault Codes
Outdoor LCDs
Indoor Display 1 2 Red 3 Green 4 Yellow
E0 ID PCB Fail On Off Off Off Connected to Power
E1 Comms Fail Off Off Off Off Power or OD PCB Fail
E2 Power Abnormal On On Off Off Comms Fail
E3 ID Fan Fail On On On On Standby
E4 OD Sensor Fail On Off Off On Compressor Overcurrent
E5 ID Sensor Fail On Off Flash Flash OD Air Sensor Fail E5
E6 Inverter Module On Flash Off Flash OD Pipe Sensor Fail E5
P0 IPM Protection On On Flash On OD Power Supply P1
P1 OD Power Supply On Off On Off IPM Protection P0
P2 Compressor Hi Temp On Off On On Compressor Temp P2
P3 Outdoor Low Temp On On Off Off Comms E1
P4 Inverter/Compressor Fail On On Flash Flash Inv / Comp Fail P4

thojas
13-12-2010, 02:17 PM
HI ,

Could anyone help with error code on York HEKB18FS-AAA? M/W split unit.
The unit runs for about 30 seconds then shuts down. The Timer & Pre Defrost LED's are flashing.