04-05-2010, 07:26 AM
could anybody tell me anything about i want to make blast freezer with condensing unit hsn 7471-75

nike123
04-05-2010, 07:31 AM
Blast freezer construction doesn't start with condensing unit. It finishes with it.:eek:

cadwaladr
05-05-2010, 05:25 PM
more info needed,what size the room what type of product what is the temperature of the product,basically the heat load,ambient etc.

Eeram
08-05-2010, 12:43 PM
HSN7471-75 is a Bitzer Semi Hermetic Screw Compressor. You still need an evaporator, condenser and all the necessary equipment and controls to make it work.

This compressor can give 44.4 Kw at -45 Deg. C suction and 40 Deg. C Condensing with R 507A, based on 10 K suction superheat and liquid subcooling.

So, you should be able to pull down 12000 kg of Sardines from 12 Deg. C to -25 Deg. C core temperature in about 14 hours.

Freezer room size should be approximately 5 X 4 X 3.2 meter high to accommodate product and evaporator, with neccessary fans and false ceiling