hi there, anyone have any experience with this model?? having major problems with the inverter blowing - all new components in the unit; acid tested and clear; new power mains cable; inverter box re-built and tested at factory. totally bamboozeled!! cheers for any help.

Peter_1
30-04-2010, 07:39 PM
It must blow, otherwise the coil will frost up in winter.

Gingerair
30-04-2010, 10:43 PM
Check the neutral connections right through to the main supply..

Thermatech
03-05-2010, 04:21 PM
2 things that will blow any ac system inverter is
1/ compressor windings down to ground. No good just testing with multi meter you have to do mega test to prove.
2/ Power supply problem. Floating or disconnected Neutral will cause major damage to the inverter.