Hello everyone,
I'm studying new model of Hiross HPM for 1 month but I understand its control not too much (iCOM controller). :confused:
We installed Hiross HPM with iCOM control to manage the dual cooling system (chilled water lead and compressor lag). Setpoint is 22 degC (+/-1 degC)and 50%RH (+/-10%RH).
Problem
The chilled water inlet is about 8 degC. Dehumidification system can control the humidity setpoint at 50%RH. However, the inlet changes to 12 degC, the humidity goes up to 70%RH - 80%RH and the compressors cannot start to dehumidify.
Question
Can I set any parameters in iCOM to control dehumidification by starting the compressors to help chilled water when the humidity is over the setpoint?
:cool:Thanks,