Q no 1) What will be the effect if an oversized condenser condenser is used. I mean a 2Ton condenser is used in a 1TON system????


Q no 2) Secondly what will be the effect if a 2Ton compressor is used in a Ton system??

goshen
29-04-2010, 05:29 PM
Q no 1) What will be the effect if an oversized condenser condenser is used. I mean a 2Ton condenser is used in a 1TON system????


Q no 2) Secondly what will be the effect if a 2Ton compressor is used in a Ton system??


low head pressure ,system will work unstable:rolleyes:
very hi head pressure,system will work unstable:rolleyes: if the evaporator is small then you will be working on low suction as well- liquid slugging
this is info offhand there will be many more symptomes!!:eek:

mianrizwan
04-05-2010, 01:47 PM
oky thanks

desA
04-05-2010, 02:36 PM
Originally Posted by mianrizwan :
Q no 1) What will be the effect if an oversized condenser condenser is used. I mean a 2Ton condenser is used in a 1TON system????


Goshen :
low head pressure ,system will work unstable

Can you perhaps expand more on this part - oversize condenser? The low head-pressure part, I understand.

Where does the instability come from? Are you thinking on terms of driving pressure-difference across the orifice & possible hunting?

Suffolk Fridge
04-05-2010, 09:06 PM
The system will be overcondensing resulting in an unstable supply of liquid at the tev inlet.
Low head pressure without a c/fan spped controller can contribute to low pressure trips certainly on cold days.
A 2 ton compressor on a 1 ton system will result in very high discharge pressure and overheating of the compressor providing it doesnt trip the HP safety first.
Are these theoretical questions or are you building a system like this?

goshen
04-05-2010, 09:35 PM
i hope not,!!