View Full Version : Maximum Starting Current



weeliang82
28-04-2010, 04:16 AM
Dear all, :eek:

Please help me on the following:

What is the maximum starting current of a system (AHU connected to two condenser units) if we know the maximum starting current of each component:

Maximum starting current of evaporator fan = 74 Amp

Maximum starting current of condenser fan = 21.75 Amp (Number = 2 condenser fans)

Maximum starting current of compressor = 125 Amp (Number = 2 compressors)

Is the maximum starting current equals the total of maximum starting current of each component?

Thanks.

goshen
28-04-2010, 05:06 AM
Hi as a rule of thumb the answer is yes!
if u have inverter compressors or fans the picture is different.
it would be recomended to start componnents one at a time .

weeliang82
28-04-2010, 05:49 AM
Meaning, the maximum starting current is 367.5 Amp..

Seems like the amp is a bit outrageous..

Brian_UK
28-04-2010, 11:45 PM
Your maximum is 125amp as stated by yourself.

nike123
29-04-2010, 04:15 AM
Depending on sequence of turning ON of electric loads, maximum starting current is sum of running current of already turned on loads and starting current of load which is currently on starting.