I repaired a morgue refrigerator back in january.as of yesterday the box is running hot @ 60 degrees. Pressures are good no bubbles in the sight glass i am thinking restriction but in january a new txv and drier were installed no temp drop accross the drier. I need feed back please on a few possibilities to look for.

Gary
27-04-2010, 01:25 AM
You might want to start here:

http://www.refrigeration-engineer.com/forums/showthread.php?t=19701

sors
28-04-2010, 11:07 PM
Thanx i figured it out box @ 38 degrees

Gary
29-04-2010, 02:13 AM
Thanx i figured it out box @ 38 degrees

Congrats... what was the problem?

sors
29-04-2010, 11:23 PM
Found a kinked liquid line that was hidden with insulation