View Full Version : Troubleshooting help
I repaired a morgue refrigerator back in january.as of yesterday the box is running hot @ 60 degrees. Pressures are good no bubbles in the sight glass i am thinking restriction but in january a new txv and drier were installed no temp drop accross the drier. I need feed back please on a few possibilities to look for.
You might want to start here:
http://www.refrigeration-engineer.com/forums/showthread.php?t=19701
Thanx i figured it out box @ 38 degrees
Thanx i figured it out box @ 38 degrees
Congrats... what was the problem?
Found a kinked liquid line that was hidden with insulation