View Full Version : AHU not responding correctly to the TAC BMS panel.



Aqeelhassan
26-04-2010, 08:09 AM
I've 3 Carrier AHU's who are not responding correctly to the TAC BMS control system.
if the unit is turned off by time programming with the TAC panel it gets off but the status still shows running and the actuator does not shutoff.
i've checked and cleaned the sensors but it did not work, please advise how to rectify.

Brian_UK
26-04-2010, 07:43 PM
Is the TAC system working correctly?

Emmett
26-04-2010, 07:52 PM
What does TAC stand for? Tour Andover Controls? If it is then the status you refer to is likely called a numeric point and would be on or off based on a program and although the unit is not running the "virtual Point" thinks it is running and that virtual point is likely controlling your actuator.

goshen
26-04-2010, 09:02 PM
hi check communication cable to the tac controller from panel.
make sure u didnt exceed the recomended distance.
What xenta model controller are u using?

Tesla
27-04-2010, 03:36 AM
Check your air press switch on ahu, this is where the status (run) should come from.

Aqeelhassan
27-04-2010, 08:18 AM
Yes, i've 13 AHU's and all response properly except 3.

Aqeelhassan
27-04-2010, 08:21 AM
I've checked and cleaned the air flow sensor.
I use TAC Xenta OP.

goshen
27-04-2010, 09:41 AM
Could be a software problem-maybe the input wasnt programed properly?

The captain
28-04-2010, 02:16 PM
Whats the front end telling you about the FCU's status?

goshen
28-04-2010, 07:12 PM
hi aqeelhassan
whats up??did u find the bug??

Tesla
29-04-2010, 12:26 AM
This point (run status) could be in the manual forced on from a software override. But from experience there is usually another fault or two. Do you have acess to manually override points on the front end or laptop? You can trace the cable from the air press switch with a bell or fset to the controller board input or mech pannel to determine if it is a software or hardware fault. I found on a big site with TAC and York AHU's that innitial commissioning was not completed - causing the CHWV to stay open when fan is not running inturn causing chiller short cycling and a very mouldy coil.

Aqeelhassan
06-05-2010, 01:15 PM
no goshen, not yet...any idea?