View Full Version : Micron gauge and vac loss



lomb
23-04-2010, 01:58 PM
I need some advice if possible please. I am installing a few small splits and purchased a vacuum gauge recently a vg64 supco. Previously i bought and used a refco digimon gauge set and hoses. However on using it to install a small split the lowest it would indicate was -930mbar or about 95% vacuum. Below this the unit does not indicate the absolute vacuum. What a load of rubbish what is the point?
Anyway for the remaining splits i bought the vg64. I have decided to bench test it so that i can get and maintain a vacuum prior to connected it to the split line sets.

So getting to the point, i have the vg64 connected to the digimon via the low line and the hi closed and then the yellow hose connected to the vacuum pump (a cc31)
After vacuuming for 20 minutes and getting down to below 250, i close the low tap on the digimon isolating the line to the vg64, i have a leak as the microns slowly increase to over 2000 over 30 or 40 minutes, i have improved the situation by putting some vacuum oil on the hose couplers and tightening. However the microns still increase. Is it possible for the hoses to be leaking, i have tried swapping with the spare hoses in the digimon kit but its the same.
Could the REFCO hoses be outgassing???
Also supco advises to use copper hoses as service hoses and for coupling the vacuum pump to the system as they say that it is unlikely rubber hoses will hold a vacuum. Please help me as im pulling my hair out at this point!:mad:

lomb
23-04-2010, 01:58 PM
Also how tight should the couplers be on the hoses should they be hand tightened or some kind of vice grip used gently? Thanks

lomb
23-04-2010, 05:34 PM
After some testing and a process of elimination i think the digimon gauges are leaking slightly on the valves. Is this for real? I shall be purchasing a ball valve shut off on Monday and isolate the outdoor unit, a hose, the vacuum pump and a ball valve.:(

lomb
23-04-2010, 11:03 PM
Can anyone tell me so i can ponder it over the weekend if i need a good set of rubber charge hoses to hold a vacuum like yellow jacket etc or will a normal set of refco hoses hold a micron rating. If so why does supco recommend against ordinary hoses?

nike123
24-04-2010, 08:57 AM
After some testing and a process of elimination i think the digimon gauges are leaking slightly on the valves. Is this for real? I shall be purchasing a ball valve shut off on Monday and isolate the outdoor unit, a hose, the vacuum pump and a ball valve.:(

Give Digimon to your kids as a toy. That is just piece of crap.
Buy TESTO or DIGICOOL digital gauges.

nike123
24-04-2010, 09:00 AM
Can anyone tell me so i can ponder it over the weekend if i need a good set of rubber charge hoses to hold a vacuum like yellow jacket etc or will a normal set of refco hoses hold a micron rating. If so why does supco recommend against ordinary hoses?

Ordinary hoses are designed for positive pressures and they are not suitable for vacuum job.
Find something like this:
http://www.appioninc.com/products/mgakitfeatures.html
http://www.appioninc.com/products/cat-tools.html

Put isolation valve and Supco vacuummeter directly on system. After evacuation is done to acceptable level, isolate system from hoses and vacuum pump and watch for pressure rise.

lomb
24-04-2010, 09:26 AM
Im in Ireland so may be tricky getting those lines. I can get yellow jacket plus 2 hoses with ball valves but it doesnt say anything on their web site about being vacuum certified.
If i purchase a ball valve isolation and 2 flare nuts for 1/4 inch refrigeration copper can i connect the service port of the outside unit to the micron gauge 1/4 sae with 1/4 liquid line and the isolation valve on the other vacuum port and then the service hoses to the digimon etc.
And yes the digimon looks like a kids toy:D

lomb
24-04-2010, 09:30 AM
The other option is to buy this http://www.amazon.com/Yellow-Jacket-18975-Vacuum-Charge/dp/B0014JDNVO
The angled one and attach the vacuum gauge to the angle off connection
How does this item connect to the outdoor valve is it just a twist on connection, and how does it attach to the service hoses? Does one have to remove the shrader core i dont want to mess with that just to save a few minutes vacuuming.

nike123
24-04-2010, 09:54 AM
Im in Ireland so may be tricky getting those lines. I can get yellow jacket plus 2 hoses with ball valves but it doesnt say anything on their web site about being vacuum certified.
If i purchase a ball valve isolation and 2 flare nuts for 1/4 inch refrigeration copper can i connect the service port of the outside unit to the micron gauge 1/4 sae with 1/4 liquid line and the isolation valve on the other vacuum port and then the service hoses to the digimon etc.
And yes the digimon looks like a kids toy:D
http://www.appioninc.com/media/videos.html
http://www.appioninc.com/distributors/locations-uk.htm

nike123
24-04-2010, 09:56 AM
The other option is to buy this http://www.amazon.com/Yellow-Jacket-18975-Vacuum-Charge/dp/B0014JDNVO
The angled one and attach the vacuum gauge to the angle off connection
How does this item connect to the outdoor valve is it just a twist on connection, and how does it attach to the service hoses? Does one have to remove the shrader core i dont want to mess with that just to save a few minutes vacuuming.

It is not few minutes, it is more than 30% faster than with cores.
http://www.youtube.com/watch?v=VWyUj9BO0U4

nike123
24-04-2010, 10:09 AM
If you are speaking of instalation of single split system and vacuuming it, than it is not economical to make vacuum leak test since it is taking time from 1/2 hour to 1 hour to confirm leak.
Just bring vacuum to 500 microns and hold there or below 10-15 min, isolate micron gauge and then release refrigerant in pipes and indoor unit until 0,5bar is on gauges. Remove gauges open service valves fully and put cap on. Switch unit to heating and check for leaks with soap bubbles at flares and valve caps. You don't need to monitor pressures since pressure alone will not tell you anything except that you have gas inside or not.

lomb
24-04-2010, 11:03 AM
Im doing my own splits so time isnt too much of a problem;)
The youtube link is very interesting and makes sense.So if i buy the valve core tool to attach the vg64 vac gauge to it needs 2 1/4 inch flare nuts and some 1/4 copper liquid line yes? Do i definately have to remove the valve core or does that tool operate the shrader valve? If need be i will remove the shrader core.
Local distributors stock the valve tool and some isolation valves so i might try that first rather than order some expensive hoses from the isle of wight.
The other option is connect the units service valve to the vacuum gauge with 2 x1/4 flare nuts and some liquid line and into the other port attach an isolation valve and then the digimon to that . I know this is slower to vacuum but will it work?
1/4 inch flare nuts that attach to 1/4 inch copper fit 1/4 inch sae flare males on vacuum gauges yes? Thanks for all the help:confused:

nike123
24-04-2010, 11:20 AM
Im doing my own splits so time isnt too much of a problem;)
The youtube link is very interesting and makes sense.So if i buy the valve core tool to attach the vg64 vac gauge to it needs 2 1/4 inch flare nuts and some 1/4 copper liquid line yes? Do i definately have to remove the valve core or does that tool operate the shrader valve? If need be i will remove the shrader core.

It does not operate shrader valve. You need to remove valve core.


Local distributors stock the valve tool and some isolation valves so i might try that first rather than order some expensive hoses from the isle of wight.They may not hold vacuum. Appion tool is certified for 20 microns.


The other option is connect the units service valve to the vacuum gauge with 2 x1/4 flare nuts and some liquid line and into the other port attach an isolation valve and then the digimon to that . I know this is slower to vacuum but will it work? It will not work, you need valve core depressor to open shrader valve on unit!


1/4 inch flare nuts that attach to 1/4 inch copper fit 1/4 inch sae flare males on vacuum gauges yes? Yes, but you cannot tighten flare nut at VG64 enough without using super thin wrench or you may broke plastic housing if wrench is not used.

It appears that vacuum tight certified hose is must or you need some adapter on VG64

lomb
24-04-2010, 12:02 PM
It does not operate shrader valve. You need to remove valve core.

They may not hold vacuum. Appion tool is certified for 20 microns.

It will not work, you need valve core depressor to open shrader valve on unit!

Yes, but you cannot tighten flare nut at VG64 enough without using super thin wrench or you may broke plastic housing if wrench is not used.

It appears that vacuum tight certified hose is must or you need some adapter on VG64


As homer simson would say DOH!
i forgot that yes the shrader will have to be depressed, so i will need that valve core tool and remove the shraders.
And yes i see your point about connecting 1/4 copper to the vg64. Im not sure if i can get a wrench on the vg64 to tighten copper to it. Il have a look. Many thanks for your help.
Ok so if i get a vacuum core tool AND one of these http://www.gascoireland.com/products/2006I06.pdf
Shut off ball valves
to connect to the vg64 and 2 1/4 inch flare nuts to connect copper to the ball valve and then the ball valve attaches to the vacuum core tool. This could work yes?
What hoses are people in the UK using for vacuum?
And if so any links?

al
24-04-2010, 03:04 PM
Lomb

I use a CPS gauge from RDL, if on a small split attach directly to manifold, as nike says achieve vacuum level and hold for as long as practical, i normally pressure test to 40B first for leakage.

alec

al
24-04-2010, 03:04 PM
Nike

Any prices on the appion manifold, looks very useful.

alec

lomb
24-04-2010, 07:56 PM
Lomb

I use a CPS gauge from RDL, if on a small split attach directly to manifold, as nike says achieve vacuum level and hold for as long as practical, i normally pressure test to 40B first for leakage.

alec

Hiya Alec
, well if my bench test experiment is anything to go by waiting for the vacuum to hold is possibly a mistake. If most hoses leak then air is reentering yes? This may not manifest when connected to an evacuated split as quickly as there is a far larger area of evacuated copper which would delay the microns creeping up as quickly. It is possible that as the hoses are new they are more permeable. Il investigate furthur on Monday and pick up some bits and report back.

al
24-04-2010, 10:14 PM
yeah, by there very nature flexible hoses will allow air ingress, the copper lines are great for larger systems, really speeds it up.

alec

nike123
24-04-2010, 10:17 PM
Nike

Any prices on the appion manifold, looks very useful.

alec
Nope, check here.
http://www.appioninc.com/distributors/locations-uk.htm

nike123
24-04-2010, 10:26 PM
Ok so if i get a vacuum core tool AND one of these http://www.gascoireland.com/products/2006I06.pdf
Shut off ball valves
to connect to the vg64 and 2 1/4 inch flare nuts to connect copper to the ball valve and then the ball valve attaches to the vacuum core tool. This could work yes?
Yes, but that ball valves could leak. You need one which is made to hold vacuum.

(http://www.yellowjacket.com/HVACRProducts.asp?t=HVACR&l=3&c=20&p=293)

al
25-04-2010, 12:55 AM
Nike

thought you had one, hence the price question, thanks anyway

alec

lomb
26-04-2010, 12:57 PM
I have ordered a cd3930
http://www.cdvalve.com/index.php?page=shop.product_details&flypage=flypage.tpl&product_id=197&category_id=10&keyword=3930&option=com_virtuemart&Itemid=60

And after opening the VG64 i can access the brass fitting safely to apply countertorque while attaching some flared 1/4 inch copper.

Will the core removal tool read vacuum with the ball valve closed and the manifolds isolated?

lomb
04-05-2010, 10:37 PM
I set it up today on the bench with a length of copper and a couple of flair nuts and this set up seems to be vacuum tight.:)