nova
15-03-2005, 11:02 PM
Yes, yet another "freezing" trivia.

Well, this is from real life.
We had this one customer to complaint that whenever he was delivering chilled goods in the first comp while the second comp was off, he first had normal heating capacity. But the heating capacity reduced soon after so that he actually didn't have any heating capacity at all.

- Unit was RD-TLE (this case applies to Spectrum TS too)
- Setpoint +4°C
- Ambient from -10°C to -20°C

What problem in a system was causing this?

Latte
16-03-2005, 01:11 AM
Faulty LLSV bleeding gas off to the rear evap :confused:

Regards

Fatboy

Reeferjon
16-03-2005, 08:30 AM
I Take it that as it applies to both RDTLE and TSS we can rule out RTPS?

chemi-cool
16-03-2005, 05:20 PM
I would like to know something about these units,
Do they heat using heat pump or electric heaters?

Chemi :)