View Full Version : Relief Valve Maintnenace Requirements



Doug1234
15-04-2010, 05:49 PM
What are the requirements for testing or replacement of relief valves in refrigeration service. These are inline valves with NB stamps usually manufactured by Henry or Mueller?

james10
15-04-2010, 08:03 PM
Henry recomonends replacing their valves every five years also the larger chiller manufactures state the same

martinw58
15-04-2010, 09:46 PM
valves need to be relaced every five years

allpro
25-05-2010, 02:35 PM
i have seen these valve last 10 years but, it needs to replace every 5

martinw58
25-05-2010, 09:45 PM
insurance companys ask for them to be replaced every 5 years

henrytech
31-08-2010, 08:38 AM
Hi guys
I work for Henry and keep a look out in this site for any issuse i can help with.

I have seen our valves last about 10yrs, BUT we recommend changing every 5 yrs. this is in line with EN13136 Refrig standards. Also note some isurance companies say to change every 3 yrs.